You may find it difficult to get agreement to eliminate color coding
and use all three wires from the same spool. Assuming you use a more
conventional color coding of two colors (Red/White/White or
Blue/Yellow/Yellow, etc.), these will need to come from different
spools. Make sure the wires are the same gauge and stranding. The
mismatch error can be expected to be a maximum of 5% of the resistance
of the run, so the wire gauge used should be larger (lower resistance
per unit distance) for minimal error when direct connecting long runs.
You can compare this error to the amount of change in resistance per
degree your sensor provides to determine whether this error is
significant.
There are other potential sources of error with long runs that may need
to have twisted and shielded cables to eliminate them. Signal
conditioning such as a 4-20 mA transmitter can eliminate the need for
anything more than a twisted pair of wires, which may substantially
lower wiring cost vs.a long run of large gauge shielded cables. You
also receive the benefits of the signal conditioning to linearize the
sensor output and can even calibrate out sensor errors to make all
outputs match.
You might also find that you do not need a 3-wire connection to your
transmitter if you can mount the transmitter close to the sensor. This
can allow the sensor to be built smaller or more ruggedly with only two
internal wire connections.