Explosion proof vs. Intrinsically safe

Last post 02-14-2011, 3:28 AM by Marcus_CorDEX. 10 replies.
Sort Posts: Previous Next
  •  04-04-2005, 10:33 AM 25

    Explosion proof vs. Intrinsically safe

    Does anybody know the difference between explosion proof and intrinsically safe? Geeked [8-|]
    "We are the dream makers and the dreamers of dreams..."
  •  04-04-2005, 4:18 PM 30 in reply to 25

    Re: Explosion proof vs. Intrinsically safe

    Explosion proof, according to the National Electrical Code, applies to an apparatus enclosed in a case that is capable of withstanding a gas or vapor explosion. It means that, should there be an explosion, it will be contained within an enclosure.

    The definition from FM Global says:

    Intrinsically Safe Circuit:  A circuit in which any spark or thermal effect, produced either normally or in specified fault conditions, is incapable of causing ignition of a mixture of flammable or combustable material in air in the mixture's most easily ignited concentration. 

    Therefore, Intrinsically safe means that an apparatus, such as a temperature transmitter is not capable of causing an explosion.  Explosion proof means that should an explosion occur, it will be contained within an enclosure.

    Paradise [ip]

  •  04-05-2005, 3:36 PM 40 in reply to 30

    Re: Explosion proof vs. Intrinsically safe

    If you are not sure which is required, you can use intrinsically safe devices in an explosionproof assembly and cover all the bases. Typically, a barrier is also required; companies like Stahl, Pepperl & Fuchs, and MTL make those.
  •  04-06-2005, 11:46 AM 53 in reply to 40

    Re: Explosion proof vs. Intrinsically safe

     MktgGenius wrote:
    If you are not sure which is required, you can use intrinsically safe devices in an explosionproof assembly and cover all the bases. Typically, a barrier is also required; companies like Stahl, Pepperl & Fuchs, and MTL make those.

    What exactly is a barrier? Why is it needed?

  •  04-07-2005, 8:14 AM 61 in reply to 53

    Re: Explosion proof vs. Intrinsically safe

    A barrier is a device, usually zener diode based, that prevents voltage spikes from entering the safe zone.
  •  04-21-2005, 8:16 AM 141 in reply to 30

    Re: Explosion proof vs. Intrinsically safe

    Confused [*-)] Color me "confused". How does a spark NOT cause "ignition of a mixture of flammable or combustable material in air in the mixture's most easily ignited concentration"? I thought that intrinsically safe meant that the energy to a circuit was limited, so that a spark could never form in the first place. I thought that the function of the barrier was to prevent accidental voltage spikes from propagating to the hazardous area.

  •  04-21-2005, 1:46 PM 145 in reply to 141

    Re: Explosion proof vs. Intrinsically safe

    We have both here(United States) with processes and equipment from all over the world SO we've had to learn both. Intrinsic safety basically means one can go into a plant, disconnect the IS wiring(blue colored here), make and break the wiring connection all day long and nothing will go KA-BOOM Lightning [li] because there is not enough energy. Here are some links for reading:

    One GOOD one I use to explain it to new designers when they ask "Why do I have to....?". Note the wiring layout with dividers as the separation/barriers ARE important to prevent wire placement making the I.S. stuff NOT safe!

    http://www.automation.com/pdf_articles/Applying_Intrinsic_Safety.pdf

    From the WalMart of instrumentation:

    http://www.omega.com/techref/intrinsic.html

    From P&F(with advertisements!):

    http://www.am.pepperl-fuchs.com/techresources/pdf/IS_in_a_nutshell-InTech-Dec2002.pdf

    Since this facility is in the U.S., we have more ex-proof than I.S. installations. One overseas trip to Germany opened my eyes to the advantages of I.S. as the plant had NO CONDUIT!! All wire was underground(control room to process area) and then in wireways(Europe's equivalent of a cabletray?). Lots of bare wires from wireways(overhead) to field devices. Their operators must be more "careful" on the job than some I've seen here Big Smile [:D].

    Also about I.S.: make sure your plant handheld radios(if you use them) are labeled by the manufacturer as I.S or approved for use in hazardous areas so they don't cause a boom when used.

    Cell phones are a gray area BUT a close friend has relayed a tale of a vendor service engineer getting flash burns when hydrocarbon vapors around a compressor caught fire when the vendor answered his cell phone. I've turned mine off before entering a process area after my friend's story and it is now a plant safety rule here. I also leave my cell phone in my car when pumping gas(Class 1 Div 1 mostly, nice dose of benzene exceeding PEL).

    Explosion proof has been covered already in this thread. Hope this helps.


    Always thankful.
  •  04-22-2005, 10:44 AM 152 in reply to 141

    Re: Explosion proof vs. Intrinsically safe

     Gilligan wrote:

    Confused [*-)] Color me "confused". How does a spark NOT cause "ignition of a mixture of flammable or combustable material in air in the mixture's most easily ignited concentration"?

    Some sparks or thermal effect are incapable of causing ignition of a mixture of flammable or combustible material in air in the mixture's most easily ignited concentration.  FM standard FM3610 contains appenidices B, and C that deal with quantifying a spark.  The spark ignition test is outlined in section XII of FM3610.

    (http://www.fmglobal.com/approvals/resources/approvalstandards/3610.pdf

  •  05-25-2005, 6:36 AM 217 in reply to 145

    Re: Explosion proof vs. Intrinsically safe

    Make sure you use "No Spark" flashlights also.  Ray-o-vac makes one.
  •  02-01-2010, 12:10 AM 1739 in reply to 141

    Re: Explosion proof vs. Intrinsically safe

    You are correct in your understanding. However, remember that there is a minimum ignition energy required to ignite any mixture of fuel & air (say a methane & air mixture).What a safety barrier does is that it limits the energy to the circuit that is in the hazardous area, so that it is below the minimum ignition energy. If you would like to stuady it in more detail, especially to avoid confusion (hazardous area instrumentation can be really confusing if you are not trained formally in it) I will strongly recommend downloading the Hazardous Area Instrumentation e-learning course. All your doubts will vanish and you will work confidently with Hazardous Area instruments.

    Also you can refer to the excellent article on Intrinsic Safety basic concepts here.

    Hope it helps!


    http://industrialplantsafety.com
  •  02-14-2011, 3:28 AM 2035 in reply to 25

    Re: Explosion proof vs. Intrinsically safe

    The simplest way to determine between Explosionproof (called flameproof in Europe) and Intrinsically Safe is as follows;

    Flameproof. This protection concept does not prevent the ignition of gas within the flameproof enclosure but the enclosure design is such that if an explosion takes place, the cooling effect of flamepaths - specifically designed, high tolerance gaps in the enclosure - mean that by the time the expanding gas/flame propegate from inside the flameproof enclosure to the plant outside, there is insufficient energy to re-ignite the surrounding gas and cause damage to the plant.

    It is a common misconception that if a flameproof enclosure is used, it is acceptable to install any component within that enclosure, the thinking being that since the enclosure can contain and cool and explosion, anything it allowed within. This is unfortunately not that case, take batteries for example specifically secondary cells (rechargables), it is not permitted to charge these cells within an flameproof enclosure as the off-gassing produced by some cells during charging can change the gas mix within the enclosure causing the potential for a higher energy explosion and as such the calculated flamepaths may not be sufficient to cool the gas as it expands.

    Another example is the Temperature Class or Autoignition Temperature. To obtain a T-Class for your flameproof device it is nessecary to quote the overall power within it so that the test body can establish how that power will translate into an external surface temperature.

    Intrinsically Safe This protection concept relates to the limitation of power to sub-incendive levels which means that the device itself cannot create a spark or surface temperature to cause an explosion. For fixed devices located permanently in the field, this is normally achieved by using either a Zener Barrier or a Galvanic Isolator, the former requires an IS Earth/Ground the latter does not. These devices effectively limit the power available to the field device by way of a series of diodes/resistor networks which prevent an explosion.

    Again, a common misconception is that if one incorporates a barrier then the downstream device itself does not need to be certified. This is not true, each part of the system must be matched. Similarly, the term "simple device" is not an excuse for the removal of a barrier altogeter, a "simple device" - such as a basic switch - is only simple when protected by a suitable barrier.

    For handheld devices, this becomes more complicated still as we must protect the device within itself rather than relying on a high level protection device located within a safe area (barrier). Everything from the battery itself through to inductive and capacitive loads, creep and clearance and even oversized track widths must be considered when designing a handheld device intended for cerrtification as intrinsically safe.

    To cap it all off, in Europe according to the ATEX Directive there are two types of Intrinsic Safety, Ex ia and Ex ib which defines the level of safety and hence the areas within which a device may operate. Ex ia devices can deal with a double failure of the protection system whereas an Ex ib device can deal with a single failure, as such Ex ia devices can be used in Zone 0, Zone 1 or Zone 2 areas whereas Ex ib devices can only be used in Zone 1 or Zone 2 areas.

    This is not the case in the US where there is only a single level of protection covering all Classes and Divisions.

    For more information on IS vs XP, you can visit our website and look through the knowledgebase or alternatively I can send our IS vs XP explanatory whitepaper directly if you email me on marcus.halliday@cord-ex.com

    I hope this was helpful.

     

    Marcus Halliday

    CorDEX Instruments Ltd.

    www.cordexinstruments.com